[Jukebox-list] "Grounding" ?
Jay Hennigan
jay at west.net
Sun Jan 6 12:34:06 PST 2008
Ron Rich wrote:
> Hi All,
> Due to the discussion of "3 wire cords", I have remembered that I have no idea how this concept works! If someone has the answers, please inform me---
> A "3 wire" 117VAC ( also called a "U ground" ) socket having a black (or red), a white, and a green wire is said to be "grounded". The black is said to be the "hot", the white is said to be "the neutral", an the green is said to be "ground" (in the USA--colors--er, colours, differ in Europe, and elsewhere).
> The fact is that the "neutral" and the "ground" are ALWAYS tied together, somewhere, either at the building's power distribution box (Now required here, along with a "grounding rod" at least six feet long, pounded into the earth, and connected to the "green" wire), or by the power company at some point. To my way of thinking, this makes the green wire, in a "plug", un-necessary, except for the fact that the ground "pin" of all 3 wire plugs is longer, and in theory, will "make" contact prior to the hot contact.
> I become even more confused (only possible for me !), when I look at what Seeburg did from the model 100"B", thru at least the STD model. They used non-polarized, 2 wire, line cords in the B thru the LPC-1 models. However the internal power sockets were polarized. From the LPC 480, on up, 3 wire line cords, and polarized sockets were used. However, in all cases, the power cords to the "control center(s)" were non-pols ! Some of the amplifiers in the later models, when a "line cord" was used, had polarized plugs on them??? Also, the lamp cords used in the later products, tended to be the pol type.
> So my questions are--What good does the 3 wire cord do, since the white and green wires are tied together? And, Why did Seeburg ( and probably others) use the non-pol 2 wire line cords for components??
The difference in terms of the National electrical Code relates to a
groundED and a groundING conductor. A grounded conductor is one that
should be at ground potential, a grounding conductor is one which is
intended to ensure that equipment is at ground potential.
The neutral is indeed tied to earth ground at one point and one point
only within a building, usually at the main service disconnect. There
are obscure exceptions but this is close enough for this discussion.
Early on, little attention was paid to hot vs. neutral in terms of
equipment wiring. There were two wires with 110 volts between them.
The plug connected the appliance to the line, a switch was put in series
and things just worked.
The problem was that insulation would fail, things would get wet, and
faults would allow exposed metal parts to come in contact with one of
the two line wires. A person coming in contact with one of the wires
alone wasn't a problem. A person coming in contact with the hot wire as
well as a ground (water pipe, wet ground, etc.) would complete a circuit
and be shocked.
Polarized plugs were an early attempt to introduce some degree of
safety. The switch could be placed in the hot side of the line so that
when a device was off its internal wiring was connected only to the
neutral. Portable lamps could be wired so that the shell of the lamp
socket was at neutral and the button at the base was hot and switched,
but the wide neutral prong was NEVER intended to be connected to parts
that people would normally touch while operating the device, such as the
metal case of an electric drill. Such parts were supposed to be
insulated from all AC wiring.
But insulation fails, people get shocked and/or killed, and they or
their surviving relatives sue.
Three different solutions to this problem have been implemented, each
with its good and bad points.
"Double insulated" appliances. Here the appliance is designed with
extra protection so that if a primary insulation fails, a second
insulator prevents contact with live parts. Good but still not 100%
foolproof.
Grounded appliances. A third wire in the cord, green, is wired to a
groundING conductor. This connects to the exposed metal parts of the
appliance. Now if a short circuit occurs inside the appliance, the
groundING conductor ensures that the case doesn't become energized, and
the short circuit trips the breaker without shocking the operator. Also
good, but now the appliance is a ground waiting to complete the circuit
to some other defective appliance.
Ground-fault circuit interrupters (GFCI). This is a relatively new
development. They work on the idea that the current flowing out the hot
(live, phase) wire should all go through the load and return through the
neutral wire. Both the live and neutral wires are passed through a
toroid transformer core. A secondary winding goes to a solid-state
amplifier and trip relay. If the line and neutral currents balance, the
magnetic fields cancel and no voltage is applied to the amplifier. If
there is a ground fault such as a person touching the live wire and a
ground OTHER THAN THE NEUTRAL such as a water pipe or another grounded
appliance, then the current going out the hot wire will be more than the
current returning through the neutral, a voltage appears on the
secondary, the trip circuit is operated, and the circuit shut down. The
advantage is that a GFCI can be used with any appliance regardless of
polarized plug, grounding wire, etc.
You'll see GFCIs as an outlet in kitchens and bathrooms with a TEST and
RESET button, as well as built in to the plugs on hair dryers. There is
also a style that replaces a conventional breaker in a breaker box.
Getting back to jukeboxes, it is not practical to go through and
double-insulate a jukebox made in the 1950s or before. Adding a ground
wire makes sense only if care is taken to ensure that the ground from
the groundING wire (the green one) is securely connected to all of the
exposed metal parts of the box, which can be difficult. And, in a
game-room situation you have now created a big grounded object right
next to the old pinball which may not be as carefully restored and has a
fault bringing its case to 120 volts. So the guy who touches the
pinball and the now-grounded juke gets shocked (and possibly blames the
juke if he touched it last.)
A GFCI works all the time and doesn't require any modification to the
box. For Seeburgs that have a cord going to an outlet on the inside of
the cabinet like an extension cord, the GFCI can be placed inside the
cabinet, but you can also just change the outlet in the room to a GFCI
type.
Personally, I always install a grounding 3-wire cord on amplifiers when
I rebuild them. In virtually all cases, the amplifier chassis is
already bonded to the cabinet and mech, and if not it is fairly easy to
do so. A GFCI is always a good idea as well. Doing both doesn't hurt
anything.
As to your other question, the white neutral wire shouldn't be connected
to exposed metal or anything not part of the active circuit. Even
though it should be groundED, it isn't used for groundING. Treat it as
a live wire from a safety standpoint. The green wire should ONLY be
connected to metal parts that are NOT part of the active circuit, and
should be used only for groundING as a safety measure.
--
Jay Hennigan - CCIE #7880 - Network Engineering - jay at impulse.net